Forum » General Discussion » Where from the root 3 in this power Eq. Power = root 3.V.I.pf .
Topics: Where from the root 3 in this power Eq. Power = root 3.V.I.pf . on General Discussion
#1
Start by
edem kass
09-20-2013 10:58 PM
Where from the root 3 in this power Eq. Power = root 3.V.I.pf .
Where from the root 3 in this power Eq. Power = root 3.V.I.pf.
09-21-2013 01:42 AM
Top #2
Enrique Gallegos
09-21-2013 01:42 AM
root 3 is used in order to use voltage line to line instead of line to neutral voltages.
You can check at "section 2.6 from power system analisys and design by J. Duncan Glober and sarma"
09-21-2013 03:59 AM
Top #3
Bojan Močević
09-21-2013 03:59 AM
I need to say that I agree in completely with sir Enrique in aspect of his explanation of meaning of "sqrt 3" except I would like to add that value of line voltage is (sqrt(3)) times higher than value of phase voltage and I would like to add that phasor of line voltage leads in front of appropriate phasor of phase voltage which means that angle of line voltage is higher than angle of phase voltage for 30 degree.
I think that is the best option, which I would like to suggest to our colleague, is to draw diagram of symmetric order of phasors of voltages (their phasors are shifted for 120 degree in the space) and then, at the same diagram, to draw phasors of line voltages, so, as he could to compare their values and angles and to easier understand behaving of phase voltages and line voltages in AC three phase power system.
09-21-2013 08:21 AM
Top #4
Enrique Gallegos
09-21-2013 08:21 AM
You right Mr. Bojan...thanks for the additional explanation.
Regards
09-21-2013 10:39 AM
Top #5
SIVAKUMAR K
09-21-2013 10:39 AM
Three phase power is actually 3 x single phase power. Single phase power is Vph x Iph x pf. So, three phase power is: 3 x Vph x Iph x pf.
In star connected networks, Vph = VL/Root 3 and Iph = IL. Thus, three phase power in a star connected network is: 3 x (VL / Root 3) x IL x pf (i.e.) Root 3 x VL x IL x pf.
Similarly, in a delta connected network, Vph = VL & Iph = IL/Root 3. Thus, three phase power in a delta connected network is: 3 x VL x (IL/Root 3) x pf (i.e.) Root 3 x VL x IL x pf.
Hope it is clear.
09-21-2013 01:06 PM
Top #6
Omer A.Osman
09-21-2013 01:06 PM
Dear Edem, as you aware V / I in AC are vectors ie they are of magnitude and direction (angle).
Therefore, in Star, 4 Wire (R,Y,B & N) was found that line voltage between R & Y is equal the sum of Vector phase voltage between R & N plus Y&N.
By mathmatical calculation (phasor)
V(RN) + V(YN) = VRY (Vectors)
V-phase as magnitude = root(3) V-line
ie magnitudes of V-phase=VRN=VYN= Root(3) V-line, and I-line = I-phase)
For delta:
I-line =Root (3) I-Phase
V-line = V-phase
Based on the above
The power in 3-phase P is
P= V-line X I-line X P.f ( Cos(phi)), phi the angle between V & I.
Since either I-line = I-phase or V-line = V-phase, not both ( depends on the connection, is it Delta or Star)
then
P = root(3) VI. p.f
By other way and further to Mr.Sivakumar comments:
Power in 3-phase = 3 X power per phase
P = 3V-phaes X I-phase X p.f
either V-phase = V-line or I-phase = I-line not both.
Then
P= 3 V-line X I-line/(root3) X p.f
= Root(3) VI.p.f
09-21-2013 03:36 PM
Top #7
edem kass
09-21-2013 03:36 PM
Every comment is given me more n more understand thank 2 u all.