Forum » General Discussion » What are the specifications for instrument cables in oil & gas plants?
Topics: What are the specifications for instrument cables in oil & gas plants? on General Discussion
#1
Start by
Fatemeh Fazli
07-28-2014 05:20 PM
What are the specifications for instrument cables in oil & gas plants?
What are the specifications for instrument cables in oil & gas plants? Is it necessary for them to be flame retardant ? and for ESD cables, is it necessary to be fire resistant?
07-28-2014 07:32 PM
Top #2
Peter Barlow
07-28-2014 07:32 PM
yes to both questions, ESD (emergency shut down) try looking at NEK6006, Noskab UKOOA type for Instrumentation, general control and Eland FTP type for fire sensors gas monitors.
07-28-2014 09:49 PM
Top #3
Fernand SCHWICKERATH
07-28-2014 09:49 PM
Please, don't forget to check the electrical specifications in force at the installation site.
07-29-2014 12:03 AM
Top #4
John Stephen Silangil
07-29-2014 12:03 AM
Instrument cable specifications for Oil & gas depends on the client’s minimum requirements for the design, manufacture, testing & supply.
Here are some examples of general specifications;
Signal Cables, Single pair or triple, Multi pair or Multi triple,
Grade=300/500volt, Sheath= PVC or CSP, Armour = Steel galvanized wire, Tape= A tape bearing the approved manufacturers name and year of manufacture to be laid under or over the core wrapping, Bedding = TPE, Overall screen = Aluminum backed mylar tape, Drain wire = Copper wire under and in contact with the screen running the full length of the cable, Core insulation = PVC or EPR or XLPE, Conductor = 1.5mm2 stranded annealed tinned or bare copper, Twists = 6-8 twists per foot
Solenoid valve & small power cables, Single pair, Multi core or Multi pair,
Grade=600/1000volt, Sheath= PVC or CSP, Armour = Steel galvanized wire, Tape= A tape bearing the approved manufacturers name and year of manufacture to be laid under or over the core wrapping, Bedding = TPE, Core insulation = PVC or EPR or XLPE, Identification = Color red/black, Conductor = 2.5mm2 stranded annealed tinned or bare copper, Twists = optional
07-29-2014 02:09 AM
Top #5
Fatemeh Fazli
07-29-2014 02:09 AM
Thanks for your attention.
another question is:
Is it recommended that Low Smoke Zero Halogen cable used for Instrument cables?
07-29-2014 04:21 AM
Top #6
John Stephen Silangil
07-29-2014 04:21 AM
I heard about the LSZH although I don't have experience yet using it, LSZH has an advantage over PVC in terms of during fire, it has a low smoke property, PVC burn & melt in the fire, LSZH cable will also burn but it don't emit heavy smoke and toxins. LSZH has a restriction in temperature range of -20degC to 75degC compare to PVC has a temperature range of -50degC to 90degC.LSZH cable is also more expensive than PVC counterparts.