Topics: What are the reasons for Earth leakage current in CNC Machine? on General Discussion
#1
Start by
Jai Kumar
09-19-2013 07:35 AM
What are the reasons for Earth leakage current in CNC Machine?
What are the reasons for Earth leakage current in CNC Machine?
09-19-2013 09:49 AM
Top #2
Omer A.Osman
09-19-2013 09:49 AM
What is CNC stand for,dear?.
09-19-2013 12:00 PM
Top #3
Jai Kumar
09-19-2013 12:00 PM
@ Mr.Omer A.Osman : computer numerical control (CNC)
09-19-2013 02:38 PM
Top #4
Omer A.Osman
09-19-2013 02:38 PM
If your question about the protection, the earth leakage is required for human protection against indirect contact .
If you are questioning about the phenomenon it self, in simple way the Earth leakage current is the current passing through Earth,CPC,externeous conductive parts to complete the circuit. ie current that complete the circuit with means other than the circuit conductors (Line/Neutral).
09-19-2013 04:44 PM
Top #5
Jai Kumar
09-19-2013 04:44 PM
We are faceing a problem in our customer CNC machine. there was continous trip in machine. hence we chaged Fuse rating in ELCB. After tat issue was resolved. But we want to find the reason for this problem. Pls help Ji...
09-19-2013 07:14 PM
Top #6
Ing. Ole Knudsen
09-19-2013 07:14 PM
You very likely have a neutral conductor from the power supply, or from a motor, connected to the frame of the machine, and a separate protective earth connected to the building earthing system, creating some double path for neutral currents.
09-19-2013 10:07 PM
Top #7
Omer A.Osman
09-19-2013 10:07 PM
Dear Kummar, usually ELCB is now replaced by RCD which operates in the principle of current balance (Line & Neutral). It is classified as a Cicuit Breaker,No fuse associated therein,accordingly.
Since you have confirmed that the rating of the Fuse feeding the aforementioned M/C has been upgraded, I gues the reason is that the rating of the protective device was under estimated. ie simply, was blown due to sustainable overload .
Note: if the fuse was used in accordance to BS3036 "re-wirable fuse", a correction factor of 0.725 ought to have been applied. ie the operating current of this type of uses does not equal 1.45In as per standard.