Measuring the yellow phase of distribution transform

measuring the yellow phase of distribution transform the voltage dropped drastically off load, whiles all the other phases are normal. I tried to increase the tapping still no change,please help?:
09-07-2014 08:04 PM
Top #2
Alan Maltz
09-07-2014 08:04 PM
Abdul,

Something is grossly wrong. I would start with a noncontact thermometer and start scanning all the connections on the yellow phase, I suspect that you will find a loose connection that has developed into a high resistance point with excessive voltage drop that is now overheating. Let us know what you find.

Alan
09-07-2014 10:43 PM
Top #3
abdul conteh
09-07-2014 10:43 PM
Okay I'll try and will let you know.
09-08-2014 01:00 AM
Top #4
Reg Millett FIEAust
09-08-2014 01:00 AM
May a poor connection in the Tap Changer. Suggest taking an oil sample and get some dissolved gas analysis done. This will give an indication of any arcing within the transformer. I am assuming that the transformer is oil filled.
09-08-2014 03:51 AM
Top #5
Raghunath Rompicherla
09-08-2014 03:51 AM
I agree with Reg. It can be a loose contact in the tap switch (guess it is off-circuit tap switch).
The off-circuit tap switches are known to give contact problems if not operated for a long time.
09-08-2014 06:27 AM
Top #6
abdul conteh
09-08-2014 06:27 AM
I will be opening the transformer today to check all connections and also oul sampling will be done. will give you full updates
09-08-2014 09:17 AM
Top #7
Mujeeb Raza
09-08-2014 09:17 AM
Can you provide the following,
1) Either measuring voltage or current, the voltage drops.
2) T/F vector group.
3) Turn ratio.
4) Measure individual winding resistance value.
09-08-2014 11:24 AM
Top #8
Norman Chambers
09-08-2014 11:24 AM
On-load circulating voltage offload significant drop. This suggest. that the Transformer winding is open circuited or defective tap changer.


Kind regards