In case Copper, annealed soft-drawn...

In grounding calculation, Maximum allowable fusing temperature (Tm) is indicated (1083 degree C) in IEEE-80-2000 (Table-1-Material constants), but in calculation we have been taking 250 degree C, whats the reason behind this...Please give yours opinion.
08-26-2013 09:45 PM
Top #2
Kab
08-26-2013 09:45 PM
where strength of copper conductor is required for mechanical reasons, 250.c shall be selected. normally for calculating of riser conductor that is connected to structure by bolted connection (like as cable lug) 250.c is selected.
where there is welding connections (like as under ground earth grid) you can use 1083.c
melting point of copper is 1083.c so in my opinion, it is better consider lesser value in calculation for more reliability.
08-26-2013 09:46 PM
Top #3
Bijaya
08-26-2013 09:46 PM
It means if Grounding mesh designed for welded type connection, we will use 1083 dC input as for maximum allowable temperature. and if Grounding mesh is designed for Compression type joints connection through Nuts & Bolts, input should be 250 dC.

Again for above ground connection to structures always considered as worst case as 250 dC.

Thanks a lot.....
08-26-2013 09:46 PM
Top #4
Sinna
08-26-2013 09:46 PM
Is it safe to base calculations on melting point instead of a FOS of at least 2?.
08-27-2013 09:08 PM
Top #5
Kab
08-27-2013 09:08 PM
for more information about selecting of final temperature rise, you can refer to BS 7430 table 10 or IEC 60621-2 annex A
in BS std. maximum value of (Tm) for welded connection is consider 700.c for copper.
however, as mentioned before, (Tm) for riser earth conductor which is connected to structure or earth terminal of equipments should be consider 250.c or selected corresponding with above standards.