how we can differentiate faults and disturbances in a power system??

how we can differentiate faults and disturbances in a power system??
09-18-2013 07:17 PM
Top #2
esmail Afshari
09-18-2013 07:17 PM
disturbances will be cleared and stability returns with tripping and reclosing (auto/manual), while faults persist and continues and leading to sectionalizing for load-supply continuities. and more
09-18-2013 10:14 PM
Top #3
amina batool
09-18-2013 10:14 PM
thank you...what's about swell and sag ??fault or disturbances.
09-19-2013 01:03 AM
Top #4
Paul Haddick
09-19-2013 01:03 AM
How about really high resolution metering and recording? Swells and sags per IEEE 1159 definitions (highly recommend obtaining and reading the entire document given your questions) are disturbances of relatively short length. They normally don't cause any protection devices at transmission and distribution any "worry" -- though the customer load centers can certainly have trouble due to facility protection design (inherently more conservative).

Persistent monitoring can answer every question you could conceivably have about a power system however.
09-19-2013 03:53 AM
Top #5
S. D. Varwandkar
09-19-2013 03:53 AM
I haven't read IEEE 1159. But should one really classify swell/ sag as fault or disturbance? It is actually an undesirable condition, bordering a steady state!
09-19-2013 06:11 AM
Top #6
Paul Haddick
09-19-2013 06:11 AM
Disturbance, since sag for example really simply reflects a momentary reactive power flow caused by load (usually high starting currents for very large induction machines). Since a motor start isn't a "fault," in my opinion it would be unhelpful to call that a fault. So it would have to be a disturbance.
09-19-2013 09:07 AM
Top #7
amina batool
09-19-2013 09:07 AM
Thanks..Paul Haddick ,S. D. Varwandkar
09-19-2013 11:39 AM
Top #8
Sugeng Saputro
09-19-2013 11:39 AM
Fault, its mean short circuit phenomena and Disturbance related of power quality (sag, swell, harmonics etc.) in your system. You can get more information the differentiation if you have Digital Fault Recorder.
09-19-2013 01:44 PM
Top #9
sinnadurai sripadmanaban
09-19-2013 01:44 PM
If duration of dip/sag/fault is more,contactors will drop & many motors will come to a standstill till restat command is given.
09-19-2013 04:07 PM
Top #10
Meynardo Custodio
09-19-2013 04:07 PM
Faults are actually short circuits that trip the protective device (circuit breaker) or blows the fuse. Faults maybe: Line to Line, Line to Ground, 2 Lines to ground, or 3 phase faults (all 3 lines faulted). The protective device will trip due to the fault. Arcing faults may not immediately trip the protective device. It may take some time for the insulation to fail due to arcing and then finally trip the breaker or blow the fuse out.

Disturbances are momentary or short time, or prolonged, or maybe reccurring anomallies on the system: such as surges, voltage dips, voltage spikes, voltage swells, voltage sags, harmonics, stray current, under frequency, under voltage, etc.They are disturbing the system power quality and performance but not necessarily tripping the circuit breaker or fuses, but in some cases of extreme magnitude, it may cause the system automatic controls and protective devices to cut off the power supply in order to protect the equipment it serves.