Its possible connect a motor of 128kW, 380V, 50Hz in a grid with 440V, 60Hz.? Its the solution a VFD? I need an alternative. Thanks
09-21-2013 04:08 PM
Top #2
Bojan Močević
09-21-2013 04:08 PM
If you want to supply your motor by using power source which has different frequency than it is written at the nameplate of your motor, you need to take care about value of magnetic induction in ferromagnetic core of your motor, because of possibility of appearing of unallowed warming of ferromagnetic core which can contribute to damaging of ferromagnetic core of your motor. This fact is a consequence of entering magnetising curve into area of saturation in H-B characteristic which describes behavior of magnetic induction in depends of intensity of magnetic field. In the area of saturation, as long as you would like to increase voltage, magnetic induction will stay at the same value which is the equal with value of magnetic induction under nominal voltage. So, by increasing voltage you will have only unallowed warming of ferromagnetic core, so you need to take care about ratio of voltage and frequency:
U1/f1=U2/f2=const.
This means that if you have motor designed for 380V and 50Hz and you want to connect it into power supply with 60Hz, your maximum allowed voltage will be:
380/50=U2/60 => U2=60*380/50=456V which is higher than 440V
So, as you can see after calculation, you can supply your motor with 440V and 60Hz.
09-21-2013 06:34 PM
Top #3
Raymond Lee
09-21-2013 06:34 PM
Vstarting torque is reduce proportional to I^2 to 93%.
Recommend the addition of a buck/bost transformer.
09-21-2013 08:45 PM
Top #4
Omer A.Osman
09-21-2013 08:45 PM
Yes you can, but you will not get the Design paramaters (Torque , speed & current will slightly be changed)- ie speed will increase, current will increase,,,etc