Calculating 30min annual maximum demand on the substation transformer.

Need help with calculating the 30‐min annual maximum demand on the substation transformer. One of the distribution transformers of a substation supplies three primary feeders. The 30‐min annual maximum demands per feeder are,

Feeder Demand, kW PF
1 2800 0.95
2 3000 0.85
3 3000 0.90

A diversity factor of 1.15 among the three feeders for both real power (P) and reactive power (Q). I need to calculate the 30 min annual max demand on the Substation TX.
01-16-2014 02:16 AM
Top #2
Alan Maltz
01-16-2014 02:16 AM
Faisal,

You already have all the information you need. Perhaps this will help you:

http://electrical-engineering-portal.com/demand-factor-diversity-factor-utilization-factor-load-factor

Alan
01-16-2014 05:07 AM
Top #3
Jim Phipps, P.E.
01-16-2014 05:07 AM
(2800+3000+3000)/x = 1.15. Thus, x = 8800/1.15 = 7652.